I have seen in the past (on Medium Voltage Switchgear) a "CT" installed on the ground bar. This CT is evidently moitors the amout of current that might be "leaking" from the sheilds on the Medium Volt wire. This seems like a very important component within the gear in the event you have bad conductor. My question is what is this ground CT called? Is there a specific name for it?
Also it seems that recently I have seen this CT less and less on the gear packages that come through the office. Is this an expensive option to include in the pricing? Most protective relays should have the ability to accept this input... correct? Is it an option that is not taken frequently enough?
You can call it earth fault protection CT.
and
There are two usage purpose of usage see below topic for extra information.
Current transformers are often used for the dual duty of measurement and protection.
CT is used For overcurrent and earth fault protection, with elements of similar VA consumption at setting, the earth
fault element of an electromechanical relay set at 10%
would have 100 times the impedance of the overcurrent
elements set at 100%.
CT and VT function like ?ears' and the ?eyes' of the protection system. They listen to and observe all happening in the
external world. Relay itself is the brain which processes these signals and issues decision commands implemented by circuit breakers, alarms etc.
The CTs can be classified into following types:
Measurement CTs
Protection CTs
A measurement grade CT has much lower VA capacity than a protection grade CT. A measurement CT has to be accurate over its complete range e.g. from 5% to 125% of normal current. In other words, its magnetizing impedance at low current levels. (and hence low flux levels) should be very high. Note that due to non-linear nature of B-H curve, magnetizing impedance is not constant but varies over the CT's operating range. It is not expected to give linear response (secondary current a scaled replica of the primary current) during large fault currents.
In contrast, for a protection grade CT, linear response is expected up to 20 times the rated current. Its performance has to be accurate in the range of normal currents and upto fault currents. Specifically, for protection grade CT's magnetizing impedance should be maintained to a large value in the range of the currents of the order of fault currents.
When a CT is used for both the purposes, it has to be of required accuracy class to satisfy both accuracy conditions of measurement CTs and protection CTs. In other words, it has to be accurate for both very small and very large values of current. Typically, CT secondary rated current is standardized to 1A or 5A (more common).
For part(II) I dont have information.