King,
I guess my real question is if these types of grounding grids are really being designed and installed to limit step or touch potential? Other than switchyards or substations, and special cases like those covered in Article 680, I don't hear much about grounding grids being installed for that purpose.
It is my understanding that the intent in most electrical installations, other than those very high power installations like substations, if for the EGC to carry enough current so the the OCPD opens the circuit in a very short time. Of course for the time it takes the OCPD to open the circuit there many very well be a harzardous step or touch potetntial, even on 120 volt circuits.