FS and FD on table 314.16a

Status
Not open for further replies.

K2X

Senior Member
Location
Colorado Springs
A practice question ask:
A FD single gang box 2-1/8 " deep shall have a minimum volume of __ in cu.

The answer is 18 so should the question have read 2-3/8" ??

And what is a FD box and or a FS box???

Thanks for all the help!!
 

cadpoint

Senior Member
Location
Durham, NC
The total volume of the cubic inches of the wires involved will be just that.

As they get respectively counted!

If the cubic inches of wire exceeds the cubic inches of a box volume, then one will go up in the size of a box.

Dont' forget to add the device count
 
Last edited:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
FD- F deep, FS- F shallow, can't remember what the F is for. I agree with you the dimension should have 2 3/8" as it appears in T314.16(A).
 