I saw this installation in one of existing building.
Distribution panel 'A' (800A MLO, 480Y/277V), one of its CB is 400A breaker and feed panel 'B'.
Distribution panel 'B' is rated at 400A MLO, 480Y/277V and contains these branch breakers:
400A
200A
100A
Even panel 'B' is not overloaded, will 400A breaker in panel 'B' be acceptable? Because panel 'B' is also fed out of a 400A breaker in panel 'A'. For coordination purpose, this installation doesn't work.