Lets say we have a starter that consists of a contactor and an overload devcice. Typically with this starter we have a breaker either an instantaneous or inverse type at the starter but lets say this breaker is 100ft upstream of the actual starter. Could this breaker be considered a branch circuit breaker for this motor starter? Since it would not be listed as a combination breaker I'm guessing it would have to be an inverse type applying to the rules of 430 and not have it larger than 250% of motor rating.
Can a motor branch circuit breaker be located upstream of the contactor as mentioned adhering to the rules of motor branch circuit protection.
If this is not allowed, then I'm guessing a motor branch circuit breaker needs to be added at the starter location, and this upstream breaker is now a feeder breaker which must be rated at 125% of motor FLA?
Can a motor branch circuit breaker be located upstream of the contactor as mentioned adhering to the rules of motor branch circuit protection.
If this is not allowed, then I'm guessing a motor branch circuit breaker needs to be added at the starter location, and this upstream breaker is now a feeder breaker which must be rated at 125% of motor FLA?