For residential use, how many outlets are allowed on a 20 amp circuit for dens, family rms, dining rms, etc.
Thanks,
Wayne
Yes, I agree with others. NEC-code has no ristriction on this but As long as I have worked and designed. I have been asked no more than 6 duplex socket per circuit.
Yes, I agree with others. NEC-code has no ristriction on this but As long as I have worked and designed. I have been asked no more than 6 duplex socket per circuit for 20 ampere breaker only.
Thanks,
Wayne
Ham,,,,you make wiring a house very expensive![]()
It would be very hard to make money wiring houses putting 6 outlets on a circuit.
And how do you come by that conclusion? Is that what the handbook says is a requirement, or is it just a suggestion, or are you able to cite a code article that backs this up? Keep in mind that the NEC is not a design manual.The hand book specifies no limit on residental but you have to have one circuit for every 500 sq ft.
All nec says is that for residential we allow 3 watts per sq ft for general use. 20 amps = 2400 watts so that covers 800 sq ft. That is for doing total load calculations.The hand book specifies no limit on residental but you have to have one circuit for every 500 sq ft.
Well, that's the theory. :roll:Common sense prevails.
Same here, but I'd add a separate lighting circuit to that scenario.Would share 1 with 2 kids bedrooms and 1 for master bed room.
Thats for feeder and service calculations - branch circuit calculation in residential uses wording like 'Shall not require additional calculation' or something to that effect... Off the top of the head...All nec says is that for residential we allow 3 watts per sq ft for general use. 20 amps = 2400 watts so that covers 800 sq ft. That is for doing total load calculations.
I sure hope you put in more than that. Each company usually sets up there own policy of how many.