Mark Twenhafel
Kinda' a newbie question, but here goes...
I have service-entrance conductors (3-phase) coming from the CT can into an existing gutter. From the gutter, existing split-bolt splices feed three separate disconnects hanging from the bottom of the gutter. My job is to upgrade one of the D/Cs from 100A to 200A. This requires opening the existing split-bolt connections in the gutter, after the POCO cuts the service drop, obviously.
What kind of splicing means is recommended for the gutter? And, btw, we are planning to increase the size of the gutter, but would rather not if we don't need to.
(1) Split-bolt? I've used split-bolts and tape for simple 2-wire splices before, but I'm not sure about this multi-tap in a gutter application. Can I run my line-side conductor along the length of the gutter and then use three split-bolts to splice onto my feed? Like this:
-X--------------X---------------X-------------> to CT can
D/C#1 D/C#2 D/C#3
(The ascii art isn't working, but each "X" is a split-bolt, and one D/C hangs below each "X".)
(2) Ilsco Clear Tap? Or Equivalent--what? Brand-names, please.
(3) (Don't flame me too bad!) Is it acceptable to use those little bus barsinside a J-box or gutter? My first though was to use 5 bus bars (those little ones mounted on insulating stand-offs)--one for each phase, neutral and EGC. Didn't know if having them exposed inside a gutter was acceptable. It's going on the side of a church, and I just feel a lot better having everything buttoned-up and insulated!
Thanks. Hope this makes sense.
Mark
D/C#1 D/C#2 D/C#3
Mark