ceb58
- Raeford, NC
Details 240v 1ph system. 60kw generator, 12kw UPS .93pf input .8pf output, 4ton A/C unit.
What is happening is when running under gen power the UPS will lock on to the power and work as should with about a 3.5 kw load. when the A/C starts ( not on UPS circuits) the UPS will drop reg. power and switch to batt. in a short time it will switch back to reg. power then the entire time the A/C is running the ups keeps switching back and forth from reg. to batt. The A/C when running is pulling about 40amps. The full load of the building, the communication equipment, and the A/C is pulling around 60 amps. What could be going on? The gen seems to be more than adequate to handle all the loads. I can understand the UPS droping out under A/C start up but not after it levels out.