VFD Cable

Status
Not open for further replies.

ron

Senior Member
The belden VFD cable comes in an overall non-metallic jacket. This cable gets run between the VFD and the motor. Is it legal to put this jacketed cable in a conduit as long as we don't exceed 40% fill?
Are there any VFD cables that have an MC jacket so we don't need conduit?
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
We put it in conduit all the time. You can take it up to 53% fill since it's treated as a single conductor. Take a look at Ch. 9 Tables, notes to tables #9.

Can't help you with the MC jacket though, we only buy the usual Belden type with the hard rubber covering.
 