KentAT
- Northeastern PA
I am looking over our existing installations for odorant injection systems for our natural gas pipeline and compressor station, and I am wondering if Group D is the correct material group for the areas containg the raw odorant mixture such as the pumps and injection lines.  (The bulk storage is typically an underground storage tank outside of the injection building).  Just curious, that's all.
The odorant mixture used would be similar to Scentinel N, here is MSDS: http://www.cpchem.com/enu/msds_unsecured/Import_99720_MSDS_O_ENGLISH_A_ENGLISH_A_N.pdf
I'm curious because I think we use Group D, but there is no list I could find that includes the ingredients of this mixture, and the manufacturer will not specify the NFPA material group to be used for haz area classification:
Tertiary Butyl Mercaptan
Isopropyl Mercaptan
n-Propyl Mercaptan
sec-Butyl Mercaptan
Plain old Butyl Mercaptan is on the materials list of NFPA 497 as Group C.
Another curious item is that we typically use APIRP500 drawings for a "lighter than air" vapor. However, the odorant liquid itself produces vapor having a density >1 per this MSDS, and also that of another odorant product we might use indicates a vapor density of 3.0, although they are both indicated as having "stable" reactivity at normal temperatures and pressure.
I would tend to think that the liquid would vaporize and produce a heavier-than-air vapor.
Any thoughts on whether a Group C or D would apply?
Would an area need to be classified based on the existence of the raw odorant pump (1000-1500 psig discharge) itself if the gas streams being injected into were not present?
Kent
Isopropyl Mercaptan
n-Propyl Mercaptan
sec-Butyl Mercaptan
Kent