You seem to know breakers and I apreciate your advice.[/quoetr]
Breaker are my life

That is all we do.
Yes the breaker is on a corn drying building that runs the 100HP fans so for 10 months out of the year the only load is lighting in that area, and yes it ran last year fully to our expectations. After the snowy winter was here for a while I noticed the lights were out and found the main tripped.
When load gets less than around 20% the CT's do not power the trip unit and the battery takes over (These batteries have a recall) and eventually the battery fails causing the trip unit setting to fail to minimum pick up and delays. There is a option on these for an external power supply, do you have that option?
4 other plants had the same problem with same breakers. We tried everything to get it back to reset with no luck.
These things are hard to troubleshoot in a forum like this, would be easy if it were in my breaker shop but too many things to consider to diagnose this here.
I believe SD is going to cover it under warrenty but with $$$$$ of corn in the dryer units during the fall of the year is there a more reliable breaker that would be a better choice. Doing the same thing over and expecting a differant out come bothers me.
Sadly no one makes them like they used to, the power breakers made in the 50's and 60's were built to last, and they have, with proper maintenence they will last forever. You don't see nuclear plants using the newer insulated case stuff on thier safety systems, they use the old reliable ones. Imagine if GM and Ford built cars to last 1,000,000 miles, what would happen to thier sales?
At this point replacing these with a different package does not make much sense for your plant, these problems can be fixed. Did anyone ever do any acceptance testing on these? You may want to consider getting an independent 3rd party testing company out there that specializes in these matters. I know good companies all over that can help you if you need a recommendation.