Landscape Lighting Conductor
pete m.
Ohio
If I have landscape lighting fed from a listed class 2 power source what is the minimum burial depth for the low-voltage conductors?
(this might be sort of a trick question)
Pete
For a class 2 or 3 direct burial cable I don't see where Article 725 would require you to follow 300.5.
I personally would use the burial depths listed in Table 300.5 column#5 but I don't see the code requiring this for listed Class 2 or 3 cables.
Chris
Chris
Thats exactly what I found... so I suppose there is no minimum code required burial depth:roll:
Pete