Working on a quote for a design/build job, for a local grain handling elevator. They are planning a expansion, that will basically have two or three stages.
Currently they have a 1200A service, 120/230V Open delta. These loads will have to be re-fed through a buck transformer. The current addition will include about 572 HP. The third will include 922 HP. TOTAL of 2000 HP.
I figure about 2656 amps by table 430.250, or 2246 amps by the following equation 2000 HP X 746 / 480V X 1.73 X .80 PF = 1,492,000/664.32=2245.9
I am curious if I am calculating this right. Service needs to be sized for all motors to run/operate at full load at once, so I dont see how you might derrate this value.
SUPPOSEDLY....the other EC pricing this job says a 1200 A 277/480V service will work, however it may be slightley overloaded.
Currently they have a 1200A service, 120/230V Open delta. These loads will have to be re-fed through a buck transformer. The current addition will include about 572 HP. The third will include 922 HP. TOTAL of 2000 HP.
I figure about 2656 amps by table 430.250, or 2246 amps by the following equation 2000 HP X 746 / 480V X 1.73 X .80 PF = 1,492,000/664.32=2245.9
I am curious if I am calculating this right. Service needs to be sized for all motors to run/operate at full load at once, so I dont see how you might derrate this value.
SUPPOSEDLY....the other EC pricing this job says a 1200 A 277/480V service will work, however it may be slightley overloaded.