kingpb
Senior Member
- Location
- SE USA as far as you can go
- Occupation
- Engineer, Registered
I assumed that if the wire has to be sized for 125% of the FLA, the terminations had to have the same capacity.
Edit: I can't cite a code reference: It just never occured to me the lugs might be allowed to be less than the conductor ampacity.
Steve
The bus or copper behind the lugs will probably only be capable of the FLA of the machine, cost savings I'm sure, or as some would say, value engineering, which is a fancy way of saying cheaper (not necessarily equal or better)