Something I ran in to on checking motor rotation last summer. A storm dropped a tree and wiped out the POCO lines feeding one of our sewer plants. I told a fellow electrician to go check the rotation on a few motors in a building that we knew the rotation wouldn't kill stuff. He came back out and said everything was cool, right rotation.
I didn't know he only checked one motor. It was on a VFD! VFD's, at least everyone I have ran in to, don't care about rotation. Flipped the breakers for the rest of the buildings.
Five years ago we asked for the money to install phase monitors on all of the motors and they told us the plant will be off line in a year, "we don't need to spend the money." Five one years....
Several thousand $'s of damage. Two days of repair and installing phase monitors on every motor in the plant........