Fire Alarm

Status
Not open for further replies.
there is a condo complex, 23 differnet buildings, with 23 different, stand alone fire panels.

do the panels need to be on a dedicated 120v circuit. they are battery packed up, and monitors by a company.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

Yes, under the 2008 NEC 760.121(B) requires an individual branch circuit to supply a power limited fire alarm system.

Chris
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Correct, this was a change in the 2008 NEC to require an individual branch circuit to supply a power limited fire alarm system.

Chris

However, NFPA 72-2002 states in part:

4.4.1.4.1 Dedicated Branch Circuit A dedicated branch circuit of one of the following shall supply primary power:
(1) Commercial light and power

There is no vertical bar next to this section, meaning that it dates back to at least the previous edition in 1999.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
However, NFPA 72-2002 states in part:

4.4.1.4.1 Dedicated Branch Circuit A dedicated branch circuit of one of the following shall supply primary power:
(1) Commercial light and power

There is no vertical bar next to this section, meaning that it dates back to at least the previous edition in 1999.

Correct, my comment was based only on the NEC.

Chris
 