- Simi Valley, CA
That does not relieve of the max 6 switch disconnect rule.
Yes it does. In some of the older panels you had MLO so if you had six disconnects and added an A/C later, you don't have to replace the panel.
Sorry, I missed that question. No, they are not split bus panels. Was federal pacific the only company to make split bus panels as thats the only brand I have run accross?You never answered the question" Are these split bus panels?"
OK, I can see the exception as not requiring individual protection for the existing panelboard. I don't see that the exception allows one to exceed the six disconnect rule as provided in 230.71.
By the way, what code cycle are we talking about? Must be 2005?
Yes 2005.
The exception that allows you to not have a main is the same one that allows more than six disconnects. You start at the six disconnect rule and you end up in the main not required. Remember you only need a main if you have more than six disconnects, so this exception is saying that you don't in an existing residential service panel.
Also while I know it's not code, look at the comentary in the handbook. And one more time for those that are hard of reading, I KNOW IT'S NOT CODE.
Yes 2005.
Here's the commentary. The phrase "for existing installations" in Exception No.2 refers to the existing panelboard. It is not intended that a split-bus panelboard used in an individual residential occupancy be replaced if a circuit is added to the existing panelboard.
OP said panel is not split bus.
And I'm not sure why the commentary says split bus. 408.36 does not mention split bus nor does 230.71.
Maybe because a split bus panel was legal at the tome. A split bus obeyed the 6 switch rule. But a MLO panel full of breakers coming straight off a meter can was wrong to start.
Maybe this got passed the way Mcclary said. Put in 6 breakers, pass inspection, and then go back and fill the panel up.
You can imagin as an inspector how well it would go over when I told the home owner that just put in that $6000 A/C system that they were going to have to spend another $3000 for a service change even though the panel would handle the additional load.
I won't say that that's not possible, but I have whole tracts of houses here with Zinsco panels and no mains in them, built in the 60's and 70's.
Could be an interesting question for the CMP on what the true intent was.
Like I mentioned before the exception simply says "lighting and appliance branch-circuit panelboards". Makes no mention of split-bus. The code section says that it can't be feed by more than two main circuit breakers. which to me means one or two.