Demand Charges

Status
Not open for further replies.

tom baker

First Chief Moderator
Staff member
Most POCOs have a demand charge for loads larger than a certain amount, say 50 KW. Its measured over a 15 minute period. Are the meters fast enough to pick up the inrush on a motor starting? Question is will a softstart or VFD reduce the peak demand?
 

cschmid

Senior Member
I believe not unless you are starting several motors in consectitive over the same required period of time. I do believe how ever it will lower the total usage just by taking the short bursts of high consumption away.
 