When doing some gardening barefooted I was going to remove the gutter downspout to put in a rainbarrel. I was holding the metal shank of the screwdriver to scratch the pain off the screw head. That's when I recieve 120VAC...After the cussing binge slowed, I got my meter out...Sure enough there was 124VAC from the gutter to the copper sprinkler head located nearby.
Also, I measured 35VAC from gutter to porch light case. And it did trip a GFCI. One breaker would eliminate the 120volts. That was yesterday.
Today, 2.5 to 7.5VAC gutter to gnd BUT we found the metal foil radiant barrier was at the same voltage. the 120VAC was never seen again.
The electrician and I checked a lot of things with nothing conclusive:
- no loose bonding/gnd in panel
- several things made the voltage fluctuate some but always in the 2.5 to 7.5 VAC range.
New roof about 4 months ago.
No ground rods in subdivision. Assuming (!) cold water ground.
Oncor came to check service entrance, no issues he could see other than there was a ~2VAC difference pre and post meter.
Let me know what steps besides:
-cable locate
-install gnd rod and attach to panel
Regards
When doing some gardening barefooted I was going to remove the gutter downspout to put in a rainbarrel. I was holding the metal shank of the screwdriver to scratch the pain off the screw head. That's when I recieve 120VAC...After the cussing binge slowed, I got my meter out...Sure enough there was 124VAC from the gutter to the copper sprinkler head located nearby.
Also, I measured 35VAC from gutter to porch light case. And it did trip a GFCI. One breaker would eliminate the 120volts. That was yesterday.
Today, 2.5 to 7.5VAC gutter to gnd BUT we found the metal foil radiant barrier was at the same voltage. the 120VAC was never seen again.
The electrician and I checked a lot of things with nothing conclusive:
- no loose bonding/gnd in panel
- several things made the voltage fluctuate some but always in the 2.5 to 7.5 VAC range.
New roof about 4 months ago.
No ground rods in subdivision. Assuming (!) cold water ground.
Oncor came to check service entrance, no issues he could see other than there was a ~2VAC difference pre and post meter.
Let me know what steps besides:
-cable locate
-install gnd rod and attach to panel