Sorry I don't have the 08 code with me but I believe the code references are the same from 05 to 08 for this question.
I would like to know whether the following installation meets code with regards to the common grounding electrode conductor having a splice or joint:
I have a 3 story building with electrical rooms stacked directly on top of one another. The service equipment and grounding electrode system is on the first floor. I have a common grounding electrode originating at the the electrode system and terminating on a copper busbar (2"x4") with a listed connection (lug) in the electrical room on the second floor. Then each of the transformers on the second floor have a tap conductor that is connected to the busbar with a listed connection.
Here is the question:
Can I then connect the third floor busbar to the common grounding electrode conductor by extending it with lugs at the second floor busbar and terminating with lugs at the third floor busbar. Or would this violate the last sentence of 250.30(A)(4)(c)? Basically would lugging the common grounding electrode conductor on a busbar be considered a splice or joint?
TIA
TIA