I am confused a bit with these questions
1. What happens in differential protection , if CT reaches it?s knee voltage point? When do such cases occur and what is the solution for stopping the relay from picking up in such cases?
++++++++++++++++++Relay++++++++++++++++++++++++++++++++++++
CT and VTs are the sensors for the relay.
CT and VT function like ?ears' and the ?eyes' of the protection system. They listen to and observe all happening in the external world. Relay itself is the brain which processes these signals and issues decision commands implemented by circuit breakers, alarms etc. Clearly, quality of the relaying decision depends upon ?faithful' reproduction on the secondary side of the transformer.
when the CT reaches it's knee voltage point there is problem of going the CT to saturation point. One of the major problems faced by the protection systems engineer is the saturation of CT on large ac currents and dc offset current present during the transient. When the CT is saturated, primary current source cannot be faithfully reflected to the secondary side. In other words. Also, the magnetizing impedance falls down during saturation. Then the transformer behaves more like an air core device, with negligible coupling between the primary and secondary winding. The high reluctance due to the air path implies that the magnetizing impedance (inductance) falls down.
So, the main engineering job is to not let the CT to go in saturation point in calculation and design work.