There are currently debates ongoing concerning grounding satellite dishes for tv.
What does code say about grounding dishes mounted on tripods in mdu's?
Can satellite installers put in there are own ground rods?
If you could also supply relevant code Numbers that would be helpful.
Article 810.21 will require a dish to be grounded, and if the distance is over 20' to the service grounding electrode system (800.40(A)(4) ) then you must install a electrode within 20' of the dish and bond it with a #6awg back to the main grounding electrode system for the building (810.21(J)
Now as I believe your are talking about multiple dwelling units (MDU's)
like putting a dish on a balcony of a second or third story apartment, I can see the frustration at trying to properly ground a satellite dish, in most cases tenets have no authority to be running grounding conductors across property that they don't control (pay rent for) and about the best they can do is try to sneak a grounding conductor down to a ground rod and hope they don't get caught.
I cases like these I don't know the options as they would have to be treated on a case by case base.
If I was a paid installer and was asked to install a dish in a situation like this, I would probably tell them unless I have access to run my grounding conductor from the dish to a installed electrode and then run a #6 bonding conductor back to the main service grounding electrode system, I could not install the dish, this is because of the liability if the dish were to take a lightning strike and caused a fire I would be up a creek without a paddle when the insurance lawyers came knocking in court.
Always cover yourself and do it by code or you could find your self in court without a defense.