What does code say about the need of bonding the equipment ground bar to the chassis of the breaker box on a sub-panel, that is connected to the main with EMT conduit?
What does code say about the need of bonding the equipment ground bar to the chassis of the breaker box on a sub-panel, that is connected to the main with EMT conduit?
Even better, in case someone feels that a panelboard enclosure isn't a box :roll:, is 408.40. "... The terminal bar shall be bonded to the cabinet and panelboard frame, if of metal, ..."
We all know that by definition it isn't.
It's a cabinet.
If the equipment ground bar is already factory installed in a panel, is it already bonded by the screws they used to factory install it or do you have to add some sort of bonding device to it?
If the equipment ground bar is already factory installed in a panel, is it already bonded by the screws they used to factory install it or do you have to add some sort of bonding device to it?