Not to be critical of you in any way, but IMHO that is not a valid scientific basis for this requirement.  Indeed, it is my belief that there is no valid scientific basis!  I would be happy to see it removed.  Consider this:
 
Case #1:
Run a 20 amp circuit 150 feet, using #12 wire and a #12 EGC.  Postulate a fault at the load end.  There will be some amount of fault current.
 
Case #2:
Run another 20 amp circuit 150 feet, using #10 wire and a #12 EGC.  Postulate a fault at the load end.  The amount of fault current will be more than in Case #1.
 
Case #3:
Run another 20 amp circuit 150 feet, using #10 wire and a #10 EGC.  Postulate a fault at the load end.  The amount of fault current will be more than in Case #1, and more than in Case #2 as well.
 
Discussion:
If we know that the fault current is higher in Case #2 than in Case #1, and therefore the chances of tripping the breaker are greater, why do we need to increase the fault current even more, by making the EGC bigger, as in Case #3?  What makes anyone think that the fault current in Case #2 was not enough, given that the installation of Case #1 was legal, and that its fault current was enough by itself?  
 
I don?t get it.  :-?