680.25 (b) 1-2 & 680.26 (b) 1-7

Status
Not open for further replies.
I was called to R&R a 240v/7.5A pool pump. The pool system is 15+ yrs. old and home owner installed. I believe that I found several violations. But I not clear in how to define 680.

1) To me, 680 reads that motor needs to be bonded with a solid #8, along with the rest of the electrical pool equipment or would a #12 be to code?

2) There's no grounding electrode for the remote sub-panel.

3) The sub-panel is mounted on a fence (no roof or cover) less than 3' off the concrete deck.

4) The Sub-panel is a Zinsco.

Any input would be helpful.

Mark
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I was called to R&R a 240v/7.5A pool pump. The pool system is 15+ yrs. old and home owner installed. I believe that I found several violations. But I not clear in how to define 680.

1) To me, 680 reads that motor needs to be bonded with a solid #8, along with the rest of the electrical pool equipment or would a #12 be to code?
Bonding would need to be by a #8 minimum
2) There's no grounding electrode for the remote sub-panel.
Not necessarily a rquirement unless this is considered to be a seperate structure
3) The sub-panel is mounted on a fence (no roof or cover) less than 3' off the concrete deck.
How far is the panel from the edge of the pool ?
4) The Sub-panel is a Zinsco.
Bad news but not a Code violation
Any input would be helpful.

Mark
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
almost ditto. How long ago was the ground rod needed at a separate structure. The zinsco panel may have been installed before the code on this.

Let me clarify. A #12 is sufficient as the EGC for the pump. The #8 is only for the equipotential bonding-- i.e. tying all the metal parts related to the pool, together. The #8 does not need to go to the panel.
 

Cavie

Senior Member
Location
SW Florida
almost ditto. How long ago was the ground rod needed at a separate structure. The zinsco panel may have been installed before the code on this.

Let me clarify. A #12 is sufficient as the EGC for the pump. The #8 is only for the equipotential bonding-- i.e. tying all the metal parts related to the pool, together. The #8 does not need to go to the panel.

Dennis, you stole my thunder!
 
Dennis, you stole my thunder!

Bonding would need to be by a #8 minimum

Not necessarily a requirement unless this is considered to be a separate structure
NO structure. Just a fence. But separate from service panel.
How far is the panel from the edge of the pool ?
>20'
Bad news but not a Code violation

almost ditto. How long ago was the ground rod needed at a separate structure. The zinsco panel may have been installed before the code on this.

Let me clarify. A #12 is sufficient as the EGC for the pump.
EGC, Please define for me?
Forgive me if I did separate quotes wrong
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
almost ditto. How long ago was the ground rod needed at a separate structure. The zinsco panel may have been installed before the code on this.

Let me clarify. A #12 is sufficient as the EGC for the pump.
EGC, Please define for me?
Forgive me if I did separate quotes wrong

EGC = equipment grounding conductor. That would be the ground wire you pull into the conduit to ground the pump. Is that what you wanted to know?
 
May I summarize my understanding:

The #12 Ground I installed from the new pump motor to the panel is to code?

The Zinsco N.G. but code.

There should be a #8 grounding electrode conductor to pool equipment (ladders, diving boards etc.) but not needed if the motor(s) are grounded with #12.

A new #8 conductor should be connected to a grounding electrode.
 

Cavie

Senior Member
Location
SW Florida
May I summarize my understanding:

The #12 Ground I installed from the new pump motor to the panel is to code?

The Zinsco N.G. but code.

There should be a #8 grounding electrode conductor to pool equipment (ladders, diving boards etc.) but not needed if the motor(s) are grounded with #12.

A new #8 conductor should be connected to a grounding electrode.

yes #12 is code and a must.

yes Zinsco is code

#8 BOND (not electrode conductor) bonding all metal within 5' of the pool. No ground rod used.

#8 must always be used.
 