Can I apply table 220.56 - demand factors for kitchen equip to laboratory refrigerators? The refrigerators are not large (1920VA at 120V) and are intermittent in use similiar to kitchen ref's.
thanks in advance.
Can I apply table 220.56 - demand factors for kitchen equip to laboratory refrigerators? The refrigerators are not large (1920VA at 120V) and are intermittent in use similiar to kitchen ref's.
thanks in advance.
I would not treat them the same way (and I don't think the code lets you anyway). If you trip the power source to dwelling unit fridges, it will destroy food, and that could cost a few hundreds of dollars. If you trip the power source to lab fridges, it will destroy lab experiments, and that could cost tens of thousands of dollars. I would design the lab to power all of them at the same time.The refrigerators are . . . intermittent in use similiar to kitchen ref's.
Can I apply table 220.56 - demand factors for kitchen equip to laboratory refrigerators? The refrigerators are not large (1920VA at 120V) and are intermittent in use similiar to kitchen ref's.
thanks in advance.
I doubt very much if you can apply NEC Table 220.56 to a refrigerator load. NEC Article 220.56 state's that these demand factors shall not apply to air-conditioning equipment. NEC 440 put's air conditioners and refrigerators in the same category.