Can someone point me to the section in the NEC that defines the minimum clearance between 5kV energized conductors and an unenergized surface in a cabinet or enclosure?
I might be misinterpreting your question. But my take on it is that cabinets and enclosures are manufactured items. The NEC does not apply to such things.
490.24O.k. but is there a section in the NEC that gives guidlines for these clearances in areas other than manufactured cabinets or enclosures? Maybe a general clearance rule?
490.24
cf
You're welcome.Thats exactly what I was looking for. Thanks!
Is there a table that corrosponds to 480V as well?