B Big Guns Member May 6, 2010 #1 Do you size up your supplemental ground conductor to the size of your largest service conductor,
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 6, 2010 #2 Big Guns said: Do you size up your supplemental ground conductor to the size of your largest service conductor, Click to expand... What is a supplemental ground conductor? If you mean GEC then yes. Remember that a ground rod only needs a #6 max.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) May 6, 2010 #3 You mean a supplemental grounding electrode for the water pipe? Yes, table 250.66. As Dennis stated ground rod only need up to a #6 and a CEE only needs up to a #4.