exit signs
In NFPA,life safety code 7.10.1.2 exits. It saiz exits other than main exterior exit door. That are obviously and clearly are identifiable as exit,shall be marked.Does this mean that all the hunreds of exit signs i been putting up over the years over the glass store fronts could have been avoided?
Most building code are more restrictive. Here is a sample from 2006 IBC
SECTION 1011 EXIT SIGNS
1011.1 Where required. Exits and exit access doors shall be marked by an approved exit sign readily visible from any direction of egress travel. The path of egress travel to exits and within exits shall be marked by readily visible exit signs to clearly indicate the direction of egress travel in cases where the exit or the path of egress travel is not immediately visible to the occupants. Intervening means of egress doors within exits shall be marked by exit signs. Exit sign placement shall be such that no point in an exit access corridor or exit passageway is more than 100 feet (30 480 mm) or the listed viewing distance for the sign, whichever is less, from the nearest visible exit sign.
Exceptions:
1. Exit signs are not required in rooms or areas that require only one exit or exit access.2. Main exterior exit doors or gates that are obviously and clearly identifiable as exits need not have exit signs where approved by the building official.3. Exit signs are not required in occupancies in Group U and individual sleeping units or dwelling units in Group R-1, R-2 or R-3.4. Exit signs are not required in dayrooms, sleeping rooms or dormitories in occupancies in Group I-3.5. In occupancies in Groups A-4 and A-5, exit signs are not required on the seating side of vomitories or openings into seating areas where exit signs are provided in the concourse that are readily apparent from the vomitories. Egress lighting is provided to identify each vomitory or opening within the seating area in an emergency.