I have an RFI in hand for a project under construction, asking whether the receptacle in an elevator control closet (non-dwelling unit) needs GFCI protection.  I thought that since the receptacle in the elevator pit is always GFCI, perhaps the one in the control closet should be too.  Now I can't find proof that the one in the pit requires GFCI!  I will require it on my designs, regardless of whether the NEC requires it, since the elevator pit is often a nasty working environment.  But neither 210.8 nor 620.23(C) nor 620.24(C) seems to require it, and I thought it was a requirement.  What am I missing?  
	
		
			
		
		
	
				
			
				