Agreed. Delta-Delta loses one advantage of the open Delta - the need for only two of the phases.You would have open delta/Open delta. Open wye/open delta is more common.
Are you saying the 2 3∅ primaries with no neutral can be connected in an 2 wire Open wye and the secondaries connected open delta? That is what I was picturing I did not know it was called Open wye/open delta.You would have open delta/Open delta. Open wye/open delta is more common.
Nope. Can't do it without the neutral. All you have is a single-phase line-to-line voltage.Are you saying the 2 3∅ primaries with no neutral can be connected in an 2 wire Open wye and the secondaries connected open delta?
In that case the primary neutral connection floats?
You can obtain 120/240 1ph with a single-phase source, whether its line-to-line or line-to-neutral.And the a secondary center tap neutral can be grounded to stabilize load side voltage to ground and feed some 120V loads?