As I understand it, no arc flash analysis is needed below 240V in accordance with 130.3 Exception 1.
Now, I assume that to mean the following:
The AFB is 4ft [following 130.3(A)(1)]
The shock hazard should be assessed per task according to Table 130.7(C)(9) and proper PPE used
Is this correct?
If someone is stabbing a breaker into a 120V lighting panel, they must wear rubber gloves and leather covers and a face shield? (category 1 according to table)
Please advise.
Thanks!
Addendum: What is the difference between:
heading: 600V switchgear
"work on cc's with energized electrical conductors and ckt parts below 120, exposed" -- category 0
heading: panel boards or other equip rated 240V and below
"work on energized electrical conductors and ckt parts, including v testing" -- category 1
the control circuit part or the voltage testing? why is on higher than the other?
Thanks
Now, I assume that to mean the following:
The AFB is 4ft [following 130.3(A)(1)]
The shock hazard should be assessed per task according to Table 130.7(C)(9) and proper PPE used
Is this correct?
If someone is stabbing a breaker into a 120V lighting panel, they must wear rubber gloves and leather covers and a face shield? (category 1 according to table)
Please advise.
Thanks!
Addendum: What is the difference between:
heading: 600V switchgear
"work on cc's with energized electrical conductors and ckt parts below 120, exposed" -- category 0
heading: panel boards or other equip rated 240V and below
"work on energized electrical conductors and ckt parts, including v testing" -- category 1
the control circuit part or the voltage testing? why is on higher than the other?
Thanks
Last edited: