Took off a car dealership last week. Very LIMITED Specications, no project manual at all. I sent questions to the architect/engineer(?) such as Tin Plated CU or AL on bussing for gear - Answer Either Heavy Duty or General Duty Disconnect Switches - Answer Either Is MC an acceptable wiring method. Answer as long as it conforms with NFPA 70 (NEC).
One item that was in fact on the drawings stated PVC could be used as stub up in boxes AND PANELS - Call me old school if you wish, but normally we do that with EMT or GRC transition (to panels receptacles at 18" AFG PVC in and out) So my question esteemed carriers of the electical flame. Does NEC allow installation of PVC (Schedule 40 or 80) within a building? If so would you please point me to the code article allowing this. We normally on feeder conduits install GRS Elbow and the transition to either EMT or GRS int to panels and use PVC on the branch circuits.
I am being lazy, but would really like feedback on this one.
Be safe out there, one second of inattention, can cause a lifetime of pain OR a loss life - We work with the invisible and it waits for our inattention to teach us it can kill us.
Steve
One item that was in fact on the drawings stated PVC could be used as stub up in boxes AND PANELS - Call me old school if you wish, but normally we do that with EMT or GRC transition (to panels receptacles at 18" AFG PVC in and out) So my question esteemed carriers of the electical flame. Does NEC allow installation of PVC (Schedule 40 or 80) within a building? If so would you please point me to the code article allowing this. We normally on feeder conduits install GRS Elbow and the transition to either EMT or GRS int to panels and use PVC on the branch circuits.
I am being lazy, but would really like feedback on this one.
Be safe out there, one second of inattention, can cause a lifetime of pain OR a loss life - We work with the invisible and it waits for our inattention to teach us it can kill us.
Steve