250.53.G and 250.56
Chamuit
Grumpy Old Man
Texas
If you installed 2 ground rods horizontally in a 2.5 ft deep trench, would they need to be 6ft apart or could the be end to end?
A. <----grnd rod----><--6ft--><----grnd rod---->
B. <----grnd rod----><----grnd rod---->
I'm curious as to what the inspectors here think.
Friday, an inspector allowed "B" because I had "met the intent of the Code." Of which, I was greatful because it took two days with a jack hammer just to dig the 16 ft x 30" long trench in the granite bedrock.
That's a really interesting question. I believe he sympathised with you and let this slide. IMO, even in those rough terrains, horizontal, the 6' rule still applies
Although required, one has to think that ground rods installed in those conditions can't provide much of a benefit should they be called upon.
That's a pity esp. since ground rods are almost worthless. I do believe the intent is to be 6 feet apart from the end of the rod. The code does not say when the rods are vertical it needs 6', but rather they need a minimum of 6'. Your installation doesn't get it.
What did they dig the footings with or is this remo work?
Existing house built in 1960 on the side of a mountain. The existing ground is the 1" water line (copper) about 6" deep (in the imported top soil) that runs around most of the house. Doing a service change.
Here's a picture of the pole that the POCO is going to replace. Shows the rock we had to dig through.
...it took two days with a jack hammer just to dig the 16 ft x 30" long trench in the granite bedrock.
Next time :roll: consider using plate electrodes. Well actually, there shouldn't be any considering to it ;) Each has to expose 2ft? [250.52(A)(7)], which is essentially a 1ft? plate. So two 16" square holes with 6' of separation plus trenching for GEC is a lot less than 16" x 30' [36' ???].
According to the "Electrical Inspection Manual" by Williams and Sargent:
A greater spacing may provide better efficiency in establishing a good connection to the earth. A common recommendation or rule of thumb is to drive multiple electrodes as far apart as they are long, but this is not a code requirement.
He must of saw the Bedrock and gave you a break.:grin:
Though that quote likely refers to rods in a vertical position. In the OP's situation,vertically speaking, they are 8' wide and 1/2" long, so they may meet the proposed 'rule of thumb" after all :cool: :grin:.