You probably had no other wires or loads involved in mind, too.DISCLAIMER:
Please do not try this experiment at home. When I gave the "nothing" answer, I based that answer on the intent to touch the two wires to each other, without touching either wire with your hand.
You would have a violation of 310.4.
DISCLAIMER:
There will be a very small amount of current that flows when you connect the two wires together, assuming that there is load on the panel bus. This current will be driven by the voltage drop between the two connection points on the bus.
One time 'something might happen' is if you're using the old Challenger tandem breakers that made it possible to energize the two wires from opposite (or different) phases. They came with the bus-bar attachments in either 'left-' or 'right-handed', so adjacent breakers could have 240 (or 208) volts between them.
I have a handful of GE half-sized breakers that have the stab clip like that one. They aren't made for bridging the space between bus stabs the way others are, like quads and half-sized FP 2p breakers, to obtain 240v.
it's actually interesting, the reason i ask is because it should be nothing...
but the information and knowledge on this site is staggeringly better than the information i get from my peers...
Since you have a freeway named after you, :grin: you should be getting the very best of information... You are a famous guy where I live.
Actually, the way to do that is to feed one conductor at the near end of the string, and feed the other conductor at the far end of the string. In total, three wires are needed for each string, one of which has no fixtures tied to it; it just feeds the far end.This is called the loop method and is used to keep incandescent light at the same light level for long lengths of runs.