I work for a large computer manufacturer and we are going to be coming out with a piece of gear that has 480V/150KVA input power on one power cord. One of the engineers was at one of our install sites chatting with the facilities engineer and the facilities engineer wanted to know if he had to assure the fault current was not capable of exceeding 10KA, he had planned to coil wire to do this. He claimed he was required to limit the fault current to 10KA unless the end equipment was rated for higher. Nobody here has heard of rating our equipment for an interrupting capacity. Cannot find in the NEC or UL950 (the end equipment safety standard we use) where is mentions anything either.
It is reasonable to expect this computer will be installed on a circuit with >10KA fault capacity, but I am not aware of anything we can/should do to rate the equipment as such. Where in the code can I go to dismiss this concern?
P.S. The equipment has an AC compartment with a line filter after it which feeds a bunch of power modules, each power module has fuses rated for 100KA interrupting.