Bare . Ok
Green. Ok
I thought #6 an smaller ,if it have insulation have to be green!!!
4 and larger you can reidentify with no problems. ( green tape or paint )
 
Bare . Ok
Green. Ok
I thought #6 an smaller ,if it have insulation have to be green!!!
4 and larger you can reidentify with no problems. ( green tape or paint )

We are talking about the grounding electrode conductor not the equipment grounding conductor. The code does not specify the need for bare or green coloring. It can be bare or it may be insulated but it does not require marking.
 