I am looking to use a connector on a Z-purged panel in a Class 1 Div 2 area.
The signals are all 24 Vdc or lower (RTD's, NAMUR proximity sensors, and thermostat contacts). NEC code 501.105 (B) 6 - appears to apply to this situation allowing me to use a non hazardous rated connector. Although item 3 of this section states : The power supply cord does not exceed 3 ft. Would these low level signals be considered the power supply cord ? - hence be limited to 3 ft ? (note I am using Class 1 Div 1 multiconductor cable to a field junction box which has the sensors wire to terminals) the cable will be hardwired into the junction box about 30' away.
The signals are all 24 Vdc or lower (RTD's, NAMUR proximity sensors, and thermostat contacts). NEC code 501.105 (B) 6 - appears to apply to this situation allowing me to use a non hazardous rated connector. Although item 3 of this section states : The power supply cord does not exceed 3 ft. Would these low level signals be considered the power supply cord ? - hence be limited to 3 ft ? (note I am using Class 1 Div 1 multiconductor cable to a field junction box which has the sensors wire to terminals) the cable will be hardwired into the junction box about 30' away.