necnotevenclose
The NEC talks about ambient temperature and derating, but where does the NEC clarify how I determine the ambient temperature?
Good luck. Apparently there is a chart that supposedly gives an ambient temp. for different areas of the country. I have no idea where it is or if it is even pertinent to the NEC.The NEC talks about ambient temperature and derating, but where does the NEC clarify how I determine the ambient temperature?
True, but not relevant to the question. He wants to know what temperature to use, such as whether he can use 30C, or whether he needs to use 35C or some other number, based on the location of the project.. . . NEC cable is based on 30 degree and ambient temperature factor for 30 degree is 1.
That is not true. Derating a cable because it is installed in a hot area is a completely different thing than derating a cable because there are too many other conductors in the same conduit. A given installation might require one derating factor or the other, or it might require both, but they are handled separately.It applies in the number of cable increases more than 3.
ASHRAE is the document to find temeprature data.
True, but not ----
That is not true. Derating a cable because it is installed in a hot area is a completely different thing than derating a cable because there are too many ----.
I just use common sense. If I'm installing something on a black roof top I figure it's going to get hot in the summer so take a guess and derate accordingly. If you're in AZ and you'r putting stuff on a black roof top it's gonna get damn hot so better add in a little more for temp.