Question on Landscape Lighting....

Status
Not open for further replies.

jango

Senior Member
With regards to exterior Low Voltage (12v) landscape lighting where outdoor direct burial transformers are used and are fed directly from indoor switching, is the primary (120v) side of the system "required" to be GFCI protected per the NEC? Any assistance on referencing the code book regarding this topic would be appreciated.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
With regards to exterior Low Voltage (12v) landscape lighting where outdoor direct burial transformers are used and are fed directly from indoor switching, is the primary (120v) side of the system "required" to be GFCI protected per the NEC?
If it's plugged into an exterior receptacle, yes.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
No it does not if they are direct wire, however if this is residential and your wire is uf and only 12 inches deep then yes you would need GFCI protection.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Jango or Dennis, in my "sheltered" life I have not seen a system where the transformer is buried. Can you provide me a manufacturer so I can study ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Jango or Dennis, in my "sheltered" life I have not seen a system where the transformer is buried. Can you provide me a manufacturer so I can study ?

Just do a search. Here is one

beverlyhillselectric_2102_16089050
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
thanks, my section of rural TN doesn't see much landscape lighting....:)
(unless the headlights on the required "vehicle on blocks" counts)
 

WinZip

Senior Member
We do quite a few in ground LV transformers an we have them GFCI protected , cost just a little more to do it right and to be safe.
 

Bjenks

Senior Member
Location
East Coast of FL
The GFCI won't do any good on the secondary only on the primary side. The transformer will have a UL listing associated with it. Based on the listing the manufacture will tell you if it needs to be GFCI protected or not. I normally don't specify GFCI for hardwired outdoor transformers.
 

WinZip

Senior Member
Safety is the main issue here , I would have it GFCI protected because you never know who might work on it an get themselves hurt , just my two cents worth.
 

Bjenks

Senior Member
Location
East Coast of FL
Safety is the main issue here , I would have it GFCI protected because you never know who might work on it an get themselves hurt , just my two cents worth.

Hopefully they still put a breaker on it:) If you put a GFCI on it then the burial depth is 12". Without GFCI then you got to dig down 18". That extra digging has got to be worth the cost of a GFCI.
 

WinZip

Senior Member
If UF or in PVC and GFCI protected it only needs to be 12 in deep at residential property but even if it where deeper still put on GFCI receptacle or breaker, I must be missing something here, all I know is why go min code on equipment outdoors when it takes just a little more effort to make it safe.
 

WinZip

Senior Member
Off topic but this happen today, I stopped by one of the jobs an one of my guy's was under the house running a circuit ( WITH OUT SPLICE ) and had his walkie talkie an was taking to the lead guy as I arrived , what he found was a broken fitting on a 1 in water line an the whole house near one end was flooded ,so I run to get channel locks an turn off the main water at the street and get the home owner out side to explain what was going on , so she calls her plumber an he shows up later for the repair but also my guy found duck work that had been broken loose by a workman at some time an also about 10x10 foot area of insulation had fallen or had been taken out so I told her about that also,she was so thankful and said guy's like you an your men are a dieing breed because she said there had been others under the crawl over the last month doing odd things an no one ever mention any of what I described above, and some of us old timers are a dieing breed from some of the crap I have seen out here.

Please don't think I'm blowing my own horn because that's not the case
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If UF or in PVC and GFCI protected it only needs to be 12 in deep at residential property but even if it where deeper still put on GFCI receptacle or breaker, I must be missing something here, all I know is why go min code on equipment outdoors when it takes just a little more effort to make it safe.

Gee and all the time I have relying on the NEC to decide safety for me. Boy, I now know better.... In all seriousness WinZip, how much safer is it to have a GFCI protecting a transformer that is direct wired and 24" deep. Heck, with that thinking we should GFCI every circuit everywhere.
 

WinZip

Senior Member
Dennis,
someday I think we will see everything Arc Fault and GFCI protected , I just choose to GFI protect a situation like that transformer feed.
 