Red Wiggler
Is there a "rule of thumb" concerning the insulating properties of air? In other words is there something to go by such as 1000 volts needs 1" of clearance to ground? 480 volts = 1/2" to ground, etc?
Well read page 4-133 art 250. in the Standard Handbook for Electrical Engineers . There is a chapter on Paschen,s air density effects on dielectric strength . Read this very good and a chart and graphs !
But hands on 1 inch can handle a lot more the 1000 volts but its all about what voltage at what pressure and whats between the charge points .
This is just personal information below do not use this for you work i play with high voltage as a hobbie !
Take 15000volts AC 1/4 inch gap it will cross at 1/2 of a inch it will not cross at 60 ma if you increase the freq it will be less and start to pass the gap at less distance between the points .
When we test high voltage cables we rap the terminal ends with sandwich rap its very thin in mills but 70 000 volts ACwill not pass thur 4 raps of this thin layer .Now in free air at 30000 volts AC it will bleed of into the air you can hear it hissing you can see it spark the gap at 50000volts ac but it depends on many different conditions .
Actually a air blast is used to stop a flow or spark in high voltage heat makes a good path for flow but a cool blast of air will put it out
Take care
I was once told that 10,000 vac would not pass through two wraps of 33. Okay Myth busters,,,is that for real?
You're a real rap artist. :grin:We use HVBT tape on medium voltage buss bars when we splice switch gear together one full rap at 1/2 lap does it . Its rated for 5 kv to 15 kv one rap and they have 35 kv tape that does the same .