mcelweec@gmail.com
CMAC1
- NYC
- Electrician
is a fire pump service sized based on the FLA or the 6 times rule?
While 6 times FLA is a rule of thumb for locked rotor current, you should use either the marking on the fire pump or table 430.251(B).
Service fire pump disconnect switch 6 times of the FLC showing in the table 430.250 for 3 phase motors( need to carry the LRC of the motor )
Wire Size 125% of the FLA showing on the motor name plate + 100 % of the sociated load ( jokey pump)
Voltage droop up to 15% is allowed .
i have a generator capable of handling 125% of fla but not 600% do i have to replace the generator?
The pressure maintenance (jockey) pump is NOT an accessory load, but is separately considered at 125% per NFPA 70-2005 695.6 (C) (1). You also can't tap the jockey pump controller conductors from the fire pump controller per NFPA 20-2007 10.3.4.8. The OCPD must carry the LRC for both the fire pump(s) and jockey pump(s) and the FLA for the "associated fire pump accessory equipment".