Proximity of switches to tub

Status
Not open for further replies.

Dustin Foelber

Senior Member
Good Evening Gentlemen
I have a project where I have a pocket framed in for a tub. There is no shower head. The GC has asked me to locate a switch bank at 46" AFF on the wall opposite the plumbing but still about 5" into this tub pocket. Switch can easily be operated while still standing in the tub. Having trouble finding code addressing switch locations. I found height reqs. but not locations. Any thoughts?
Thanks
 
What do you say about this

404.4 Damp or Wet Locations.
A surface-mounted switch or circuit breaker in a damp or wet location shall be enclosed in a weatherproof enclosure or cabinet that shall comply with 312.2. A flush-mounted switch or circuit breaker in a damp or wet location shall be equipped with a weatherproof cover. Switches shall not be installed within wet locations in tub or shower spaces unless installed as part of a listed tub or shower assembly.
 
Status
Not open for further replies.
Top