8 b boxes
can you use an 8B boxes for a ceiling Fan?
or does it have to be a 1900 with a square to round ring ?
It all depends on how you support the fan. I usually have a block of 2x4 or 2x6 behind an octagon. I use 3" wood screws to support the fan indepently of the box.
What is a 8B box? I know the other is a 4" sq. with ring.
Either one, as long as it complies with 314.27(D).
Boxes at Ceiling-Suspended (Paddle) Fan Outlets. Outlet boxes or outlet box systems used as the sole support of a ceiling-suspended (paddle) fan shall be listed, shall be marked by their manufacturer as suitable for this purpose, and shall not support ceiling-suspended (paddle) fans that weigh more than 32 kg (70 lb). For outlet boxes or outlet box systems designed to support ceiling-suspended (paddle) fans that weigh more than 16 kg (35 lb), the required marking shall include the maximum weight to be supported.
Dennis: This
is an 8b box.
I wouldn't trust the 8-32 cover screws to support the fan. You need a fan-rated box (and use the hardware that comes with it), not just any metal octagon (8b) box, if the box is supporting the weight.
Larry,
I agree with you
"I wouldn't trust the 8-32 cover screws to support the fan. You need a fan-rated box (and use the hardware that comes with it), not just any metal octagon (8b) box, if the box is supporting the weight."
A few years ago, I got a call from a customer, at 1:00AM, who was still in his bed, staring up at his ceiling fan! The Fan had worked loose from the box, and was hanging from the wires.
You have to use a fan rated box or you can independently support the fan as I do. I have gone to a house where the fan was hanging by the wires. It was a 36 inch fairly light fan and had been installed with a pop in box. Interestingly, the screws never gave ou but the box support worked thru the sheetrock. It was up there for years. Go figure......