John Fimbianti
can you use an 8B boxes for a ceiling Fan?
or does it have to be a 1900 with a square to round ring ?
Boxes at Ceiling-Suspended (Paddle) Fan Outlets. Outlet boxes or outlet box systems used as the sole support of a ceiling-suspended (paddle) fan shall be listed, shall be marked by their manufacturer as suitable for this purpose, and shall not support ceiling-suspended (paddle) fans that weigh more than 32 kg (70 lb). For outlet boxes or outlet box systems designed to support ceiling-suspended (paddle) fans that weigh more than 16 kg (35 lb), the required marking shall include the maximum weight to be supported.
I wouldn't trust the 8-32 cover screws to support the fan. You need a fan-rated box (and use the hardware that comes with it), not just any metal octagon (8b) box, if the box is supporting the weight.or does it have to be a 1900 with a square to round ring ?