I have an issue with a gas furnace and gas water heater that I recently installed. NEC 250.104 (B) addresses bonding of all metal piping likely to become energized within a building. My question is: Should I run a bonding jumper (say 10Awg for a 15a line - just for less resistance) from the gas line entering the furnace to the junction box containing the branch circuit for the furnace and connect it to the circuit EGC? If so, should this jumper also connect the cold water inlet? Lastly, if this must be performed on the furnace, should it be done on the H.W.H. as well?
I've asked several other electricians and have gotten several different opinions....there seems to be great confusion surrounding this issue. Some feel that it does not have to be done bcs. by default (at the service and from the utility company) these pipes are already bonded. Others feel that it must be done to eliminate potential difference if one of the two pipes were to become energized. Others feel that this will present a larger problem if an arc on the circuit were to ignite the gas.
I figure that worse case scenario I'll leave it without the jumper for now and if the inspector wants it in he'll say so. However, I need clarity on this issue and know that if anyone will know, it'll be you guys.
Thanks.
Thanks.