I installed my first auto transformer this week. I bucked 277 to 230 to operate an HVAC unit. On one of the secondary leads of the Xfrmr the voltage read around 40V to ground. If this conductor faults will it still open the OCPD?
My second question involves the KVA rating of these units. The unit I was given to install was labeled as 2 kva, yet it was rated at 50amps (or close to it) at 230V. Obviously way more than 2 kva. How is kva calculated for these? And what would be the line current of the the primary related to the secondary? I imagine the the line kva would equal the load kva plus any losses and my final question is how efficient are these units; are the losses significant?
My second question involves the KVA rating of these units. The unit I was given to install was labeled as 2 kva, yet it was rated at 50amps (or close to it) at 230V. Obviously way more than 2 kva. How is kva calculated for these? And what would be the line current of the the primary related to the secondary? I imagine the the line kva would equal the load kva plus any losses and my final question is how efficient are these units; are the losses significant?