That being said, I don't see strong enforcement of these rules when it comes to attic spaces and roof-tops which is particularly worrisome to me being in SW Florida.
But the code NEVER allows a conductor to exceed its temperature rating, even for one second.
NC gets pretty hot but I have never seen evidence of overheating in a nm cable due to attic heat. Have you?
No, but that is not the point.
That would be impossible to enforce.
That would mean the highest temp in an attic would have to used and there is no telling what that would be for a given home.
What temp would one use?
That is because it rarely gets over 120 degrees in a properly ventilated attic. If you stick to 240.4(D) and load the circuit accordingly it will NEVER exceed the 140 degree F. Self enforcing.
Thanks Bob but you totally missed the point of my post.
Jack-- you have to use the correction factor when the temps get over 86 degrees. At 120 degrees you would need a correction factor of .82 for a 90C wire. Not a problem in most cases unless there are other derating factors to consider. Once you NM cables get larger then #10 wire this can make a big difference.
You do under certain conditions. Refer to 310.15(B)(3)(a) for specifics.Why don't we have to derate for #12 Mc cable?
As for the reason behind the 'excepting' of AC/MC I have no credible idea.
Reference, please......
For non-multi-receptacle circuits the 60% derating has no affect on #12 MC cables when bundled in any quantity.