I'm looking in the code book for where it says line and low voilt can't be run thru the same bored hole. Can anyone tell me where to find it. Thanks
Interesting. Thanks. I think I've even been tagged for this
300.3(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Probably 300.3(C) is what the inspector was thinking but that is not for bored holes. We try to separate our power from communication and data lines to avoid intereference not per the NEC.
Yeah Pierre probably red tagged you.:grin:
That's not for cables either.![]()
Can you please post 300.3 (c)
Probably 300.3(C) is what the inspector was thinking but that is not for bored holes. We try to separate our power from communication and data lines to avoid intereference not per the NEC.
Yeah Pierre probably red tagged you.:grin:
I know. I think people hear you cannot put low voltage and line voltage together-- based on this article and never read what the article actually says.
Take a peak at 725.130(A) and the FPN. Yes I know fpn's are not code, just sayin...
Class 2 and Class 3 circuits on the load side of the power source shall be permitted to be installed using wiring methods and materials in accordance with either 725.130(A) or (B).
(A) Class 1 Wiring Methods and Materials. Installation shall be in accordance with 725.46.
Exception No. 1: The derating factors given in 310.15(B)(2)(a) shall not apply.
Exception No. 2: Class 2 and Class 3 circuits shall be permitted to be reclassified and installed as Class 1 circuits if the Class 2 and Class 3 markings required in 725.124 are eliminated and the entire circuit is installed using the wiring methods and materials in accordance with Part II, Class 1 circuits.
FPN: Class 2 and Class 3 circuits reclassified and installed as Class 1 circuits are no longer Class 2 or Class 3 circuits, regardless of the continued connection to a Class 2 or Class 3 power source.
What about intermixing fiber and line?
There are a few spacing requirements for communications wiring (Chapter 8) from electric power and light and other higher energy wiring, but most if not all are moot regarding everything but open conductors.It could also be a misapplication of 820.133(A)(2).
No restrictions or problems that I'm aware of (other than what Volta mentioned).What about intermixing fiber and line?