CrossfitSparky
New member
I have a project in which an engineer is requesting we run a 25kV cable as the equipment grounding conductor. Has anyone ever heard of this? It is for a bunch of circuits from a 24.9kV metal enclosed switch to a VFI, and from the VFI to various transformers. I asked if I could use an appropriately sized 600V conductor for the ground and he tried explaining something about the conductor being rated for the voltage during a fault condition. I'm skeptical of his theory, but want to make sure I do my homework before I inform a very good customer that his consultant is about to spend a lot of his money unnecessarily. I've been doing this a long time and have never heard of a voltage rating for the insulation of an equipment grounding conductor. Any input?